Its been purchased. Now I have a couple of wiring questions. What size wiring and circuit breaker do I need to run if I had the motor wired for 220. It can also be wired for 110
motor specs
HP 1.5
RPM 3450
Volt 115/208-230
FLA 13.4/7.4-6.7
SF 1.30
SFA 17.6/10.3-8.8
phase 1 type b
thermally protected.
My suggestion is to put in a 20 amp 240v circuit using 12 gage wire and appropriate 20 amp connections and breaker. That way, you're setup for something larger should you decide to upgrade in the future to a 2 or 3 hp unit.
--
The most expensive tool is the one you buy "cheaply" and often...
No problem at all. You could also put in 10 gage and terminate with 20 amp, leaving the option to upgrade to 30 amp later merely by changing the breakers and other terminations to the proper rating later. Any 240v circuits I've installed since the original have been with 10 gage for exactly that reason.
--
The most expensive tool is the one you buy "cheaply" and often...
motor specs
HP 1.5
RPM 3450
Volt 115/208-230
FLA 13.4/7.4-6.7
SF 1.30
SFA 17.6/10.3-8.8
phase 1 type b
thermally protected.
so based on the motor specs I can install 30 amp breakers, 10gauge wire, and a plug and receptacle for 30 amps? I know I'm beating this topic to death but I am want to make sure all if safe and good. Basically is overkill ever bad? Like if a went all 50amp components from motor to breaker.
Thank you. I may go 30amp for growth purposes since cost and time will be be pretty much the same anyway
Yes, the motor is immaterial to the question as long as the circuit meets the minimum requirements for that motor. Breakers protect the wire, not the machine, so oversizing is just fine.
--
The most expensive tool is the one you buy "cheaply" and often...
Thanks. I will probably go 30amp and install 6in pipes. This way if I ever upgrade, it will be just a dust collector swap